Solar/battery quote

Hi
Looking for opinions on quote I've had.
15x415w trina vertex s panels
Givenergy 5kw gen3 hybrid inverter
Givenergy AIO 13.5kw battery
£12.7k

Sounds pretty good but installer doesn't think g99 is needed where I think it is?

What do you guys think?
Cheers
«1

Comments

  • Screwdriva
    Screwdriva Posts: 1,465 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    edited 13 October 2023 at 8:28AM
    Sounds pretty good but installer doesn't think g99 is needed where I think it is?

    That's a really loud warning sign. I would walk away from them if they do not:

    1) Provide MCS G99 + HIES 
    2) State in writing that they offer the full 12 year warranty on the All in One
    3) Spec a 6kW inverter for the above 6.2kW system (assuming its all a single roof aspect)
    4) Swap out the cheap, low end (<£60 a panel) Trina for quality panel brands like Solarwatt/ Hyundai/ Sharp / REC/ Eurener / Qcells/ Panasonic/ Meyer Burger or REA.

    An attractive price can often be misused to conceal the above!
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • Thanks. Starting to think the same
  • Exiled_Tyke
    Exiled_Tyke Posts: 1,341 Forumite
    Ninth Anniversary 1,000 Posts Name Dropper
    Agree @Screwdriva except that a 5kW inverter could be about right (I read that 80% of peak is optimum for the UK) especially if panels are across two orientations (as you imply)
    Install 28th Nov 15, 3.3kW, (11x300LG), SolarEdge, SW. W Yorks.
    Install 2: Sept 19, 600W SSE
    Solax 6.3kWh battery
  • Screwdriva
    Screwdriva Posts: 1,465 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    edited 13 October 2023 at 11:36AM
    Agree @Screwdriva except that a 5kW inverter could be about right (I read that 80% of peak is optimum for the UK) especially if panels are across two orientations (as you imply)
    In my relatively humble experience, the best performing rooftop PV installation I've helped with (attached below) has 4.8kW of PV (12 X 400W Sharp panels) and a 5kW SolarEdge Inverter. Despite having only 2 additional panels than us, the site has generated 4.68 mWh year to date (vs our 3.37mWh).

    It's no surprise the owner has just asked his installer to cover the area below his dormers with more panels 

    I've found that inverter size coming in just under the installed PV capacity is a very safe bet with large, single aspect South facing roofs, especially if a future expansion of the system may be on the cards. On dual aspect roofs, the 80% rule is largely accurate. On triple aspect or higher roofs, I suspect it's even lower - our 7.3 kW tri-aspect installation still retains the 3.68kW SE inverter - we did not "clip" earlier this week, despite the clear, sunny, Indian Summer October days and a 75% increase in daily generation compared to the previous clear sunny day. 




    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • Magnitio
    Magnitio Posts: 1,188 Forumite
    1,000 Posts Third Anniversary Name Dropper
    Agree @Screwdriva except that a 5kW inverter could be about right (I read that 80% of peak is optimum for the UK) especially if panels are across two orientations (as you imply)
    Agree that a 5kW hybrid inverter is fine. There will be minimal clipping and if it is an issue, the excess can be used to charge the battery.
    6.4kWp (16 * 400Wp REC Alpha) facing ESE + 5kW Huawei inverter + 10kWh Huawei battery. Buckinghamshire.
  • Yes the roof is a bit of a jumble of aspects (after a prior extension). It would have made sense if they'd justified the lack of G99 by explaining that. Instead it was implied g99 was only for commercial installs which clearly is wrong!
  • Screwdriva
    Screwdriva Posts: 1,465 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    Yes the roof is a bit of a jumble of aspects (after a prior extension). It would have made sense if they'd justified the lack of G99 by explaining that. Instead it was implied g99 was only for commercial installs which clearly is wrong!
    Entirely disingenuous. Run, don't walk, in the opposite direction.
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • Thanks for the advice guys.
    Had a further quote through from a supplier who actually understands the need for DNO!
    8 x Jinko 435w + Tigo optimisers (across 3 different aspects S/E/W - roof mess)
    GE AIO 
    £11.4k
    or
    20 x Jinko + optimisers (12 additional on North facing roof)
    GE AIO
    £13.2k
    Extra £1.8k for 12 panels is tempting even if theyre North facing. Tell me I'm wrong.

    Thanks

  • Netexporter
    Netexporter Posts: 1,833 Forumite
    1,000 Posts First Anniversary Name Dropper
    Extra £1.8k for 12 panels is tempting even if theyre North facing. Tell me I'm wrong.

    The sun rises in the NE in summer. A nice early morning/late evening boost. As you have optimisers they should pick up a decent amount of reflected light in the middle part of the day.

    Have they supplied the modelling of what you might expect for each layout?

  • cheesesarnie
    cheesesarnie Posts: 201 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    edited 17 October 2023 at 4:34PM
    Not yet. That comes after a site visit I think (although they have said est generation 2373kw (8 panels at the back of the house) 4899 (12 additional at the front/north). 
    Just looking at the google map, the north roof is slightly off north. Not sure if thats a good thing or a bad thing.
    Never been a fan of street facing panels before but what can you do?


Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.3K Banking & Borrowing
  • 252.9K Reduce Debt & Boost Income
  • 453.2K Spending & Discounts
  • 243.3K Work, Benefits & Business
  • 597.8K Mortgages, Homes & Bills
  • 176.6K Life & Family
  • 256.3K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.