Interesting SCOP with an MVHR
Comments
-
shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.0 -
shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.0 -
waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.1 -
shinytop said:waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.
Though even without that, my DHW requirements are at least 215 kWh a month, even when it isn't winter. So, for 8 months assuming less than 2000 kWh of hot water, and a SCOP of 6, that's not a lot of money at all for 8 months.
Equally, you could get those waste water recovery thingies, and halve your DHW too0 -
waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.
Though even without that, my DHW requirements are at least 215 kWh a month, even when it isn't winter. So, for 8 months assuming less than 2000 kWh of hot water, and a SCOP of 6, that's not a lot of money at all for 8 months.
Equally, you could get those waste water recovery thingies, and halve your DHW toowaqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.
Though even without that, my DHW requirements are at least 215 kWh a month, even when it isn't winter. So, for 8 months assuming less than 2000 kWh of hot water, and a SCOP of 6, that's not a lot of money at all for 8 months.
Equally, you could get those waste water recovery thingies, and halve your DHW too0 -
shinytop said:waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.
Though even without that, my DHW requirements are at least 215 kWh a month, even when it isn't winter. So, for 8 months assuming less than 2000 kWh of hot water, and a SCOP of 6, that's not a lot of money at all for 8 months.
Equally, you could get those waste water recovery thingies, and halve your DHW toowaqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:shinytop said:waqasahmed said:DougMLancs said:The main reason their performance is so high is that they’re running at 31C flow temp with weather compensation, no buffer, no zoning on trv’s (just overheat protection and no glycol.Part of the reason that they can run such a low flow temp through their radiators is that it looks like they’ve calculated the MVHR to cover around 1400kWh of the 6345kWh heat loss based on the heat pump size being 5kW. In theory though, they could’ve skipped the MVHR and gone for a larger emitter area to have the same COP so you don’t HAVE to have MVHR to get such figures.
In our case, 8 K2’s and 1 K3 with decentralised MVHR in the kitchen and bathroom was enough for us to design to a flow temperature of 35C. Yes we could’ve gone all out with extra wall insulation and super efficient glazing first but the benefit isn’t proportional to the cost so we’ll save that for when the opportunity naturally presents itself (and there are no toddlers around!).
You can fit antifreeze valves instead but if they freeze or stick; they will empty all the water out of the system.
Or you can use nothing and hope you don't have an extended power cut when it's very cold.
I mean I wouldn't turn my radiators completely off in winter for example, purely because the pipes would potentially crack if they don't have heat going through them
I have glycol in mine because it's what the installers use as standard because the manufacturer (Mitsubishi) recommends it. If it's a little less efficient then so be it.
Though even without that, my DHW requirements are at least 215 kWh a month, even when it isn't winter. So, for 8 months assuming less than 2000 kWh of hot water, and a SCOP of 6, that's not a lot of money at all for 8 months.
Equally, you could get those waste water recovery thingies, and halve your DHW too0 -
waqasahmed said:
Though even without that, my DHW requirements are at least 215 kWh a month, even when it isn't winter. So, for 8 months assuming less than 2000 kWh of hot water, and a SCOP of 6, that's not a lot of money at all for 8 months.
Equally, you could get those waste water recovery thingies, and halve your DHW too
As I posted before it's really not clear what that heat pump is achieving at the moment. They shouldn't need heat, and flow temp is too low for DHW.1 -
Qyburn said:waqasahmed said:
Though even without that, my DHW requirements are at least 215 kWh a month, even when it isn't winter. So, for 8 months assuming less than 2000 kWh of hot water, and a SCOP of 6, that's not a lot of money at all for 8 months.
Equally, you could get those waste water recovery thingies, and halve your DHW too
As I posted before it's really not clear what that heat pump is achieving at the moment. They shouldn't need heat, and flow temp is too low for DHW.0 -
waqasahmed said:Qyburn said:You'll need a flow temp of more than 27 Deg.C for DHW.
As I posted before it's really not clear what that heat pump is achieving at the moment. They shouldn't need heat, and flow temp is too low for DHW.A 35C flow temp will give you hot water in the low 30s. Which might be OK if you like cold showers & tepid baths but wouldn't be acceptable to most people.If you buy or borrow a baby bath thermometer you can feel for yourself how warm water temps in the 30-40c range are.Most people want their DHW to be 50C or more.N. Hampshire, he/him. Octopus Go elec & Tracker gas / Shell BB / Lyca mobi. Ripple Kirk Hill member.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 30MWh generated, long-term average 2.6 Os.1 -
QrizB said:waqasahmed said:Qyburn said:You'll need a flow temp of more than 27 Deg.C for DHW.
As I posted before it's really not clear what that heat pump is achieving at the moment. They shouldn't need heat, and flow temp is too low for DHW.A 35C flow temp will give you hot water in the low 30s. Which might be OK if you like cold showers & tepid baths but wouldn't be acceptable to most people.If you buy or borrow a baby bath thermometer you can feel for yourself how warm water temps in the 30-40c range are.Most people want their DHW to be 50C or more.0
Categories
- All Categories
- 340.1K Banking & Borrowing
- 249.1K Reduce Debt & Boost Income
- 448.3K Spending & Discounts
- 232K Work, Benefits & Business
- 603.2K Mortgages, Homes & Bills
- 171.6K Life & Family
- 245.2K Travel & Transport
- 1.5M Hobbies & Leisure
- 15.8K Discuss & Feedback
- 15.1K Coronavirus Support Boards