Singing radiators after moving TRVs

6K Posts

in Energy
Driving me barmy. Not sure the other family members can hear it, it's fairly high-pitched, almost a whistling sound but not quite loud or piercing enough.
Background: Heat pump and rads were installed summer 2019. Never knew how to use the TRVs so never touched them. They have been bled a couple of times in the years since installation. The first time I adjusted the one in the kitchen, it was making the sound all the time afterwards, even at night when the heating wasn't running (though I think the water circulation pup was still going for frost protection?) That time I turned it from 6 (fully open) to about 3. After identifying the sound the next night, I put it back up to 6 and it stopped.
Few months later, taking us to last week, and the plumber doing our bathroom told us to turn all the rads off as he needed to disconnect the bathroom one, then back on once he'd done that. The idea was to not fully drain them so they didn't need bleeding, I think? We did, and the kitchen one started singing again. So I turned it down to somewhere between 3 and 4, but then the kitchen was cold for washing at night so I turned it up to full again but thankfully it was okay and din't make a noise.
This evening one of the rads upstairs is doing it (not been touched since last week). It was on 4, where the green button is. Turn it down and it got louder, turn it up just past 4 and it stopped.
Anyway, at the end of a long story: does anyone have any ideas WHY the radiators might be doing that?
[Incidentally on our Housing Association's heating page on their website, they say under no circumstances must we drain down or bleed the radiators ourselves, so that's not an option. Though once the bathroom's finished and that radiator reconnected, if the plumber doesn't bleed them I'll check the temps at the top and bottom to see if they indicate needing it.]
Background: Heat pump and rads were installed summer 2019. Never knew how to use the TRVs so never touched them. They have been bled a couple of times in the years since installation. The first time I adjusted the one in the kitchen, it was making the sound all the time afterwards, even at night when the heating wasn't running (though I think the water circulation pup was still going for frost protection?) That time I turned it from 6 (fully open) to about 3. After identifying the sound the next night, I put it back up to 6 and it stopped.
Few months later, taking us to last week, and the plumber doing our bathroom told us to turn all the rads off as he needed to disconnect the bathroom one, then back on once he'd done that. The idea was to not fully drain them so they didn't need bleeding, I think? We did, and the kitchen one started singing again. So I turned it down to somewhere between 3 and 4, but then the kitchen was cold for washing at night so I turned it up to full again but thankfully it was okay and din't make a noise.
This evening one of the rads upstairs is doing it (not been touched since last week). It was on 4, where the green button is. Turn it down and it got louder, turn it up just past 4 and it stopped.
Anyway, at the end of a long story: does anyone have any ideas WHY the radiators might be doing that?
[Incidentally on our Housing Association's heating page on their website, they say under no circumstances must we drain down or bleed the radiators ourselves, so that's not an option. Though once the bathroom's finished and that radiator reconnected, if the plumber doesn't bleed them I'll check the temps at the top and bottom to see if they indicate needing it.]
0
Latest MSE News and Guides
Replies
Thnaks
Interesting, I'll look into that, thanks. Is it something that could have shifted or moved slightly, internally, in the 4 years since installation?
IMO the best course of action would be to open up the TRV and reduce the heat pump flow temp a bit and ensure that weather compensation is turned on. Don't try using a heatpump like a conventional boiler.
The trick with a heatpump is to get it running at the lowest flow temp you can get away with to keep the house temperature fairly even and run it for longer and just use the TRVs to avoid the rooms getting over heated. Weather compensation should reduce the flow temp when its wormer outside and increase it when it gets colder to balance the heat loss.
That is interesting, and really useful to know what the mechanism is behind the whistling.
Maybe just leaving them all open like before would solve it - the setup seems to work because the thermostat is in a colder room, and the rooms that get warmer whilst the thermostat room is getting up to temp are rooms we're happy to have warmer.
No I definitely won't. I've been too scared to do the 'system off' needed to check the frost stat temperature, messing about with bits I really don't understand is not something I'll be doing!
The trouble with weather compensation is it needs lots of tweaks when it's cold to find the best settings - I don't think my family would put up with that, and the way we run it at the moment seems to be a decent balance between efficiency and comfort.