Bigmacroxy said:QrizB said:Bigmacroxy said:The reason they state is that because the array is 150 metres from the house (ground mount), the AC inverter must be located outside at the array itself and only AC taken into the house, because of DC voltage drop.This seems a bit odd but it depends on the configuration of your array.If your array is a single string, the operating voltage of your array could easily be 400VDC or more. That will have a lower loss over a 150-metre cable run than 240VAC will.
There will be two strings of 8 panels, each string with Open Circuit of 420 volts at 11 amps.
I did read from another message board that "you MUST use your highest voltage across your longest run with the thickest wire you can afford".
So I'm still ost as to why this solar company is advocating an inverter underneath the array, bringing back AC which will lose more voltage % compared to the whole.
Should I insist on DC and a hybrid inverter? I don;t want to get another supplier as the wait now is over 9 months.16 Panel (250W JASolar) 4kWp, facing 170 degrees, 40 degree slope, Solis Inverter. Installed 29/9/2015 - £4700 (Norfolk Solar Together Scheme); 9.6kWh US2000C Pylontech batteries + Solis Inverter installed 12/4/2022 Year target (PVGIS-CMSAF) = 3880kWh - Installer estimate 3452 kWh:Average over 6 years = 4400 :j1 -
G98 is up to 16A per phase, G99 is over 16A per phase8kW (4kW WNW, 4kW SSE) 6kW inverter. 6.5kWh battery.1
-
Bigmacroxy said:QrizB said:Bigmacroxy said:The reason they state is that because the array is 150 metres from the house (ground mount), the AC inverter must be located outside at the array itself and only AC taken into the house, because of DC voltage drop.This seems a bit odd but it depends on the configuration of your array.If your array is a single string, the operating voltage of your array could easily be 400VDC or more. That will have a lower loss over a 150-metre cable run than 240VAC will.
There will be two strings of 8 panels, each string with Open Circuit of 420 volts at 11 amps.Let's assume that the installer uses 6 sq. mm. cable for the 150m link. At 3 milliohms per metre per conductor, that's a total cable resistance of 900 milliohms (0.9 ohms).- 31A at 230VAC will drop 28 volts, and will lose 865 watts.
- 21A at 340V will drop 19 volts, and will lose 397 watts.
Neither of those would be acceptable in practice, but at least if you run DC and have the inverter at the house you'll have a working system. With a 28V AC drop your inverter at the array will keep tripping on high voltage.In practice you'll need to run much thicker cable with an AC system, to ensure that the inverter doesn't trip out, but however thick the cable is it will remain true that the AC system will lose more than twice as much power as the DC one.Even with 16 sq. mm. cable I think you're looking at a 10.5V drop with an AC circuit, vs. 7V with DC, and you'll still risk tripping on high inverter voltage.Bigmacroxy said:Should I insist on DC and a hybrid inverter? I don;t want to get another supplier as the wait now is over 9 months.(If there's an actual electrical engineer reading this, please correct me.)N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.Not exactly back from my break, but dipping in and out of the forum.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!2 -
G99 is for anything above the 3.68 limit up to 50MW.
London. 6.4kwh system, South facing. 16 Hyundai 400kw all black panels w/ optimisers, 6kw Solaredge HD Wave inverter, Solar Iboost with two immersion heaters on one 240l hw tank. Octopus Flux. Ivar 5 Wood Burning Stove. Leaf 62kwh plus Zappi. Two chickens: 1 Light Sussex, 1 Speckled Rock. Omlet walk-in run. Approx 1.5 eggs per day egg generation rate using Marriage's organic layers pellets.0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.3K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.2K Work, Benefits & Business
- 599.4K Mortgages, Homes & Bills
- 177.1K Life & Family
- 257.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards