Heat Pump integrated into Hot Water Cylinders (Vaillant, Daikin etc.)

Screwdriva
Screwdriva Posts: 1,412 Forumite
Fifth Anniversary 1,000 Posts Name Dropper Photogenic
edited 26 December 2022 at 12:46AM in Green & ethical MoneySaving
Seems like a sensible way to reduce hot water heating costs without going with a heat pump for the entire household. I wonder if any users/ owners are out there?

https://www.ariston.com/en-uk/products/heat-pumps/air-source-heat-pump-water-heater/nuos-plus-wifi-uk/
-  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
-  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
-  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

Feel free to DM me if I can help with any energy saving!
«1

Comments

  • QrizB
    QrizB Posts: 16,458 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    edited 23 June 2022 at 9:12PM
    Good to see another company entering this part of the market!
    A year ago I knew of two "big brand" manufacturers selling these: Tesy and Dimplex, plus the less well-known Cool Energy. I even started a (short) thread on the subject:
    The idea of using waste heat from kitchens & bathrooms is an interesting one, but in the winter the energy balance is less helpful. Most seem to have a conventional coil for thermal sources, for use in the colder months.

    Edit to add: The Cool Energy line seem to be rebadged Italian products from Styleboiler.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 33MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • Screwdriva
    Screwdriva Posts: 1,412 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    Seems to be around £1000 over a conventional option (Megaflo as an example is around £1200 for an 250L tank)


    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • Thanks, do you think it would it be a viable compliment to air-to-air heat pumps(?)
  • QrizB
    QrizB Posts: 16,458 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    Thanks, do you think it would it be a viable compliment to air-to-air heat pumps(?)
    That's one obvious application for these in a domestic environment. AAHP would otherwise leave you with direct electric water heating.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 33MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • shinytop
    shinytop Posts: 2,150 Forumite
    Eighth Anniversary 1,000 Posts Name Dropper Photogenic
     Screwdriva said:
    Seems like a sensible way to reduce hot water heating costs without going with a heat pump for the entire household. I wonder if any users/ owners are out there?

    https://www.ariston.com/en-uk/products/heat-pumps/air-source-heat-pump-water-heater/nuos-plus-wifi-uk/
    It's definitely something worth looking at. But I'm not sure this one would work in many UK homes as it appears to need to be in a room of 30m3 and has a SPL of 51/55db(A), which is more than my outdoor ASHP.   
  • Screwdriva
    Screwdriva Posts: 1,412 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    edited 24 June 2022 at 6:36PM
    shinytop said:
     Screwdriva said:
    Seems like a sensible way to reduce hot water heating costs without going with a heat pump for the entire household. I wonder if any users/ owners are out there?

    https://www.ariston.com/en-uk/products/heat-pumps/air-source-heat-pump-water-heater/nuos-plus-wifi-uk/
    It's definitely something worth looking at. But I'm not sure this one would work in many UK homes as it appears to need to be in a room of 30m3 and has a SPL of 51/55db(A), which is more than my outdoor ASHP.   
    I believe the 30m3 requirement is only if installation is ductless? 
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • 2nd_time_buyer
    2nd_time_buyer Posts: 797 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    edited 24 June 2022 at 9:46AM
    shinytop said:
     Screwdriva said:
    Seems like a sensible way to reduce hot water heating costs without going with a heat pump for the entire household. I wonder if any users/ owners are out there?

    https://www.ariston.com/en-uk/products/heat-pumps/air-source-heat-pump-water-heater/nuos-plus-wifi-uk/
    It's definitely something worth looking at. But I'm not sure this one would work in many UK homes as it appears to need to be in a room of 30m3 and has a SPL of 51/55db(A), which is more than my outdoor ASHP.   
    I believe it requires this to be ductless? 
    From the installation manual:

    "a) In the event of water heaters without an air exhaust duct, the room of installation should have a volume of no less than 30 m3 and must be adequately ventilated. "

    So if it can have a duct then perhaps it might be okay? If it was put in a cupboard the 51dBA would also be okay. It is not dissimilar from a combi boiler.

    Edit: from a quick skim of the manual it seems there are options for ducted and ductless installation.
  • shinytop
    shinytop Posts: 2,150 Forumite
    Eighth Anniversary 1,000 Posts Name Dropper Photogenic
    shinytop said:
     Screwdriva said:
    Seems like a sensible way to reduce hot water heating costs without going with a heat pump for the entire household. I wonder if any users/ owners are out there?

    https://www.ariston.com/en-uk/products/heat-pumps/air-source-heat-pump-water-heater/nuos-plus-wifi-uk/
    It's definitely something worth looking at. But I'm not sure this one would work in many UK homes as it appears to need to be in a room of 30m3 and has a SPL of 51/55db(A), which is more than my outdoor ASHP.   
    I believe it requires this to be ductless? 
    From the installation manual:

    "a) In the event of water heaters without an air exhaust duct, the room of installation should have a volume of no less than 30 m3 and must be adequately ventilated. "

    So if it can have a duct then perhaps it might be okay? If it was put in a cupboard the 51dBA would also be okay. It is not dissimilar from a combi boiler.

    Edit: from a quick skim of the manual it seems there are options for ducted and ductless installation.
    I wonder if you could divert any ducting for some free AC in the summer?
  • shinytop said:
    shinytop said:
     Screwdriva said:
    Seems like a sensible way to reduce hot water heating costs without going with a heat pump for the entire household. I wonder if any users/ owners are out there?

    https://www.ariston.com/en-uk/products/heat-pumps/air-source-heat-pump-water-heater/nuos-plus-wifi-uk/
    It's definitely something worth looking at. But I'm not sure this one would work in many UK homes as it appears to need to be in a room of 30m3 and has a SPL of 51/55db(A), which is more than my outdoor ASHP.   
    I believe it requires this to be ductless? 
    From the installation manual:

    "a) In the event of water heaters without an air exhaust duct, the room of installation should have a volume of no less than 30 m3 and must be adequately ventilated. "

    So if it can have a duct then perhaps it might be okay? If it was put in a cupboard the 51dBA would also be okay. It is not dissimilar from a combi boiler.

    Edit: from a quick skim of the manual it seems there are options for ducted and ductless installation.
    I wonder if you could divert any ducting for some free AC in the summer?
    Very good idea. I am warming (and cooling) to the idea.

  • Screwdriva
    Screwdriva Posts: 1,412 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    shinytop said:
    I wonder if you could divert any ducting for some free AC in the summer?
    I believe many owners have done this and that the cooling is substantial. 
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.7K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 452.9K Spending & Discounts
  • 242.7K Work, Benefits & Business
  • 619.4K Mortgages, Homes & Bills
  • 176.3K Life & Family
  • 255.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.