ispookie666 said:@QrizB
Will need to put scaffolding up for any change and that would be significant cost (likely a years FIT payment). Might wait till a few more degrade or die completely to consider changing them. I'll have to check the M215 micro inverter spec sheet to find out if newer panels would be ok.I did buy a very, very, long pole and gave mine a wash but it didn’t change anything.Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)0 -
JKenH said:On the east roof, which has 6 panels on each string, DC1 measured 218v and DC2 176v.On the west roof which has 7 panels on each string, DC1 was 216v and DC2 251v.OK, so that sounds like one faulty panel on each roof.
- East roof: 218 / 6 = 36.3 then 36.3 x 5 = 182 (quite close to 176)
- West roof: 251 / 7 = 35.9 then 35.9 x 6 = 215 (very close to 216)
Are these 54-cell panels? A typical 60-cell panel has a Voc of around 40V, but 54 cells will give a Voc of about 36V which is what you're seeing.In theory, the faulty panels should be hotter than the good ones (since it's not turning 300W of sunshine into electricity) but I have no idea whether you could detect that from the ground with a thermal camera or whatever.N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.Not exactly back from my break, but dipping in and out of the forum.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!1 -
QrizB said:JKenH said:On the east roof, which has 6 panels on each string, DC1 measured 218v and DC2 176v.On the west roof which has 7 panels on each string, DC1 was 216v and DC2 251v.OK, so that sounds like one faulty panel on each roof.
- East roof: 218 / 6 = 36.3 then 36.3 x 5 = 182 (quite close to 176)
- West roof: 251 / 7 = 35.9 then 35.9 x 6 = 215 (very close to 216)
Are these 54-cell panels? A typical 60-cell panel has a Voc of around 40V, but 54 cells will give a Voc of about 36V which is what you're seeing.In theory, the faulty panels should be hotter than the good ones (since it's not turning 300W of sunshine into electricity) but I have no idea whether you could detect that from the ground with a thermal camera or whatever.Voc is quoted as 39.6v for my panels. I did a Voc check on my freestanding solar panel (which I use to charge my PPS) and found it varied depending if it was in sun. Would you expect that?Edit: presumably my panels are wired in series to get that Voc so wouldn’t a failed panel affect the out put from the others? The poor string on my East roof is now around 76% of the good string.Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)0 -
@JKenH - No, just left it. My cut off would be half the panels degrading. Only need 5 more.
I am presuming it is the panels rather than problem with the micro inverter.“Don't raise your voice, improve your argument." - Desmond Tutu
System 1 - 14 x 250W SunModule SW + Enphase ME215 microinverters (July 2015)
System 2 - 9.2 KWp + Enphase IQ7+ and IQ8AC (Feb 22 & Sep 24) + Givenergy AC Coupled inverter + 2 * 8.2KWh Battery (May 2022) + Mitsubishi 7.1 KW and 2* Daikin 2.5 KW A2A Heat Pump0 -
JKenH said:Voc is quoted as 39.6v for my panels. I did a Voc check on my freestanding solar panel (which I use to charge my PPS) and found it varied depending if it was in sun. Would you expect that?Yes, shading, clouds etc. will affect Voc, and so will temperature. On a cold but bright winter's day a panel can exceed the notional Voc and so you always need a bit of headroom between the string voltage and the max inverter voltage, in case you exceed it. (This is more frequently a problem in DC off-grid systems where you pay more for higher-voltage controllers so there's a temptation tyo cut corners.)
In principle the bypass diodes will replace the failed panel with a short circuit, so the current from the good panels can still flow but wihout gaining voltage from the failed one. That seems to be what's happening here, although you might expect the loss to be 17% (1/6th) not 24%.Edit: presumably my panels are wired in series to get that Voc so wouldn’t a failed panel affect the out put from the others? The poor string on my East roof is now around 76% of the good string.N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.Not exactly back from my break, but dipping in and out of the forum.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!2 -
The degradation is gradually creeping up. For a long while it was around 17% but today it is just over 25%
Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)1 -
I hope it's just unfavorable conditions rather than deg. If the latter, that's way higher than quoted figures(I presume these were installed in 2018?).
“Don't raise your voice, improve your argument." - Desmond Tutu
System 1 - 14 x 250W SunModule SW + Enphase ME215 microinverters (July 2015)
System 2 - 9.2 KWp + Enphase IQ7+ and IQ8AC (Feb 22 & Sep 24) + Givenergy AC Coupled inverter + 2 * 8.2KWh Battery (May 2022) + Mitsubishi 7.1 KW and 2* Daikin 2.5 KW A2A Heat Pump0 -
ispookie666 said:I hope it's just unfavorable conditions rather than deg. If the latter, that's way higher than quoted figures(I presume these were installed in 2018?).Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)1
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.2K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.2K Work, Benefits & Business
- 599.3K Mortgages, Homes & Bills
- 177K Life & Family
- 257.6K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards