The DNO said no

JKenH
Posts: 5,145 Forumite

I have previously mentioned that due to an oversight a DNO application wasn’t submitted at the time my panels were installed. A retrospective application was submitted for 10kw as I wanted to add a few more panels. I have now heard back from my installer that the DNO has said we can’t export more than 5.9kw without upgrading to a 3 phase supply the rough estimate for which is about £10k.
I already have installed 4.2 kwp facing approximately WSW and 3.6kwp facing ESE. Each array has a 3.6 kw inverter. Because of the orientation of the roofs they don't peak at the same time.
Is there a device available to cap overall export from two inverters? I can live with 5.9 kw overall but I dont treally want to have to scale the inverters down individually to get to 5.9kw.
Any suggestions welcomed.
K
I already have installed 4.2 kwp facing approximately WSW and 3.6kwp facing ESE. Each array has a 3.6 kw inverter. Because of the orientation of the roofs they don't peak at the same time.
Is there a device available to cap overall export from two inverters? I can live with 5.9 kw overall but I dont treally want to have to scale the inverters down individually to get to 5.9kw.
Any suggestions welcomed.
K
Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)
0
Comments
-
What a bummer!
Are the inverters in the same location, could you switch to a single larger inverter that's capped at 5.9kW? Solaredge, just a fancy way of achieving the same.
There are some devices that cap based on export not generation, but you'll need to get the Google machine out, probably need to change inverters, and also they'll have to have been approved by your DNO, and still early days.
Possibly some battery work around, but again, will need lots of changes, and DNO approval.
I've only got the broadest thoughts and ideas here, nothing specific nor particularly helpful, sorry.Mart. Cardiff. 8.72 kWp PV systems (2.12 SSW 4.6 ESE & 2.0 WNW). 20kWh battery storage. Two A2A units for cleaner heating. Two BEV's for cleaner driving.
For general PV advice please see the PV FAQ thread on the Green & Ethical Board.0 -
I'd be thinking along the lines of a single larger inverter with the capability to cap the export at 5.9kWh.
The 3.6kWh inverters are capable of around 6.6kWh combined & with background consumption at 300w (?), the theoretical excess is currently only around 400w.
Because of the opposing orientations you're not going to peak on both inverters at the same time so I doubt you'd ever achieve 5.9kWh as things stand.....so nothing lost.4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North LincsInstalled June 2013 - PVGIS = 3400Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh0 -
Ask your DNO if they have any approved export limiting devices you could use. I live in the northwest and our DNO approves the use of ENA100 compliant devices:
http://www.energynetworks.org/electricity/engineering/distributed-generation/engineering-recommendation-g100.html
More details here:
https://www.sma-uk.com/solar-systems/export-limitation.html
It’s a sorry state of affairs that the planet is dying and people who install solar are being asked to pay to improve the grid AND export their energy for free. Surely the DNO should do grid strengthening work for free if it’s receiving free renewable energy in return?5.18 kWp PV systems (3.68 E/W & 1.5 E).
Solar iBoost+ to two immersion heaters on 300L thermal store.
Vegan household with 100% composted food waste
Mini orchard planted and vegetable allotment created.0 -
I might be wrong here but my understanding was that you could have a 3.6kw inverter so max about 5kw solar panel system without DNO. Also a 7kw system if you ha e a battery. So could you just not add a battery.6kWp system, 20 x 300W Longi Solar panels with a Solis 6.0 inverter + Wifi and iBoost
22deg pitch East to west 12 panels on the East and 8 on the West0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.5K Banking & Borrowing
- 253.3K Reduce Debt & Boost Income
- 453.9K Spending & Discounts
- 244.5K Work, Benefits & Business
- 599.8K Mortgages, Homes & Bills
- 177.2K Life & Family
- 258K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards