3.98kW from 3.5 kW system

My Geo solo II monitor showing on very sunny days even 3.98 kW but I got 3.5 kW system...is this possible? Or monitor is not very accurate?

Comments

  • nomoneytoday
    nomoneytoday Posts: 4,871 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    Probably a tolerance on both the measuring and manufacturering sides IMHO :)
  • nigelpm
    nigelpm Posts: 433 Forumite
    Part of the Furniture Combo Breaker
    Sounds like an inaccurate monitor unless you are talking the split second when the sun comes out of the clouds?
  • oldskoo1
    oldskoo1 Posts: 619 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    I noticed my 4kW array averaged 4.6kW over 15 mins according to my inverter data. The amp's were at 19A too which is interesting as the breaker is 16A.

    I can only assume its inaccurate or at certain times such as cool panels and with sudden sunshine it can spike
  • rosythfifer
    rosythfifer Posts: 92 Forumite
    Eighth Anniversary 10 Posts Combo Breaker
    I have seen my 2.43 panels putting out over 2.43 for some periods, wiboth my monitors showing the same.
    2.43 from 9 x 270 Trina panels. Samil solar river 2600 inverter. Due South. 30 pitch. East coast of Scotland just North of Forth bridge.
  • Andy_WSM
    Andy_WSM Posts: 2,217 Forumite
    Part of the Furniture 1,000 Posts Uniform Washer Rampant Recycler
    I had to have my MCB changed to 20A because at 16A it would trip occasionally. An MCB should always be rated higher than the expected current through it, so not sure why Solar electricians fit 16Amp anyway. I get that's the DNO limit for export, but that doesn't mean it should be that sized breaker! The breaker is there to protect the circuit (specifically the cable), not to restrict export to the DNO.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 353.8K Banking & Borrowing
  • 254.2K Reduce Debt & Boost Income
  • 455.2K Spending & Discounts
  • 246.9K Work, Benefits & Business
  • 603.4K Mortgages, Homes & Bills
  • 178.2K Life & Family
  • 260.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.