Saunier Duval F30E - can't repressurise
alanrowell
Posts: 5,389 Forumite
I have one of these (yes I know it's crap but I didn't install it) and the pressure has dropped so that the boiler does not run. Tried using the integrated filling loop but there was no water flow and the pressure stayed at 0.4 bar.
Did some research and replaced the Filling Valve which also contains a non-return valve but this made no difference.
So what else could it be? Could it be that the combination of pressure within the boiler plus the spring pressure from the non-return valve is too much for my mains water pressure? Or am I just unlucky in fill valves?
Did some research and replaced the Filling Valve which also contains a non-return valve but this made no difference.
So what else could it be? Could it be that the combination of pressure within the boiler plus the spring pressure from the non-return valve is too much for my mains water pressure? Or am I just unlucky in fill valves?
0
Comments
-
Are you sure the diaphragm in the expansion vessel hasn't failed?0
-
I could understand that if the expansion chamber was leaking then the pressure would drop but I'm trying to get the pressure up.0
-
Theres a pretty good clue here that the problem lies somewhere between the water source and the filling valve really.alanrowell wrote: »Tried using the integrated filling loop but there was no water flow and the pressure stayed at 0.4 bar.
Understatement of the bleeding obvious I know - sorry.
Unlikely - but have you measured it? are all valves upstream open?Could it be that the combination of pressure within the boiler plus the spring pressure from the non-return valve is too much for my mains water pressure?
Who knows?Or am I just unlucky in fill valves?
Sounds like you may need to find yourself an SD accredited service man local to you i.e. someone who knows the animal.
CheersThe difference between genius and stupidity is that genius has it's limits. - Einstein0 -
Ohh - possible lightbulb moment. Didn't leave a plastic blank in the inlet did you?
CheersThe difference between genius and stupidity is that genius has it's limits. - Einstein0 -
Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)0
-
Latest update - drained the boiler totally, then started refilling. Reached 0.4 Bar then stopped. Drained again, repeated with the old RPZ, same result. Also checked the fillingcock and there's definitely a good flow of water through it. There is water getting into the boiler - just not enough of it.Theres a pretty good clue here that the problem lies somewhere between the water source and the filling valve really.
Understatement of the bleeding obvious I know - sorry.
Unlikely - but have you measured it? are all valves upstream open?
Who knows?
Sounds like you may need to find yourself an SD accredited service man local to you i.e. someone who knows the animal.
Cheers
Another thought - could the air not be venting from the boiler when filling?0 -
I have this exact same problem with the exact same boiler! - I'm desperate to find a solution (I'm not a plumber). Please help!0
-
Same advice. Find yourself a local SD accredited tech who knows the beast to look at it for you.I have this exact same problem with the exact same boiler! - I'm desperate to find a solution (I'm not a plumber). Please help!
CheersThe difference between genius and stupidity is that genius has it's limits. - Einstein0 -
Turned out to be a blocked water pressure sensor. Once cleaned out everything worked.0
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.9K Banking & Borrowing
- 253.9K Reduce Debt & Boost Income
- 454.7K Spending & Discounts
- 246K Work, Benefits & Business
- 602.1K Mortgages, Homes & Bills
- 177.8K Life & Family
- 259.9K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards