Another boiler problem - ours is leaking

Options
Think everyone is having probs!

Our combi bolier (only 17 months old) is leaking very slightly. We're going to try and get someone out ASAP to look at it, but I wanted to know if we should turn it off in the meantime?

I'd rather not if possible as it is forecast to be -13 or so here tonight. We do have a gas fire in the lounge if needs be though.

Thanks

too many comps..not enough time!
«1

Comments

  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Hi

    What boiler would that be??

    GSR
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • chickaroonee
    chickaroonee Posts: 14,678 Forumite
    Hi thanks for responding, it's a Worcester (not sure I've spelled that right)

    too many comps..not enough time!
  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Hi thanks for responding, it's a Worcester (not sure I've spelled that right)

    You spelt it right-but which model Worcester?-there are many Worcester combis.
    Where is it leaking from?
    No free lunch, and no free laptop ;)
  • chickaroonee
    chickaroonee Posts: 14,678 Forumite
    Reading the booklet now and think it is a greenstar 25si and the bit that is leaking seems to be a "condensate connection"

    Hope that makes sense!

    too many comps..not enough time!
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Reading the booklet now and think it is a greenstar 25si and the bit that is leaking seems to be a "condensate connection"

    Hope that makes sense!

    Frozen condensate waste...more here

    HTH

    GSR
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • chickaroonee
    chickaroonee Posts: 14,678 Forumite
    Thanks! Does seem to be that, except don't have this one -

    your boiler is displaying either an EA fault code, a D5 code or is displaying a flashing blue light (for 26CDi boilers you may see a flashing red light instead)

    Does that mean we don't need to reset it? Sorry if I'm being dim!

    too many comps..not enough time!
  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Sounds like the condensate pipe has frozen, then when thawing has popped a connection in the pipe. Is the leak indoors or out? As long as the condensate is still able to drain away (which if it's 'leaking' then it must be) then you won't get an EA fault code and it's safe to use the boiler. You just need to get the joint repaired and get the pipe lagged more effectively to stop it freezing again.
    No free lunch, and no free laptop ;)
  • chickaroonee
    chickaroonee Posts: 14,678 Forumite
    It's indoors, although haven't checked outdoors yet as hadn't realised that would be relevant (sorry I'm useless!).

    Thanks very much for your help macman and canknucklehead.

    too many comps..not enough time!
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Thanks! Does seem to be that, except don't have this one -

    your boiler is displaying either an EA fault code, a D5 code or is displaying a flashing blue light (for 26CDi boilers you may see a flashing red light instead)

    Does that mean we don't need to reset it? Sorry if I'm being dim!

    Take a look outside (or where ever it terminates) and see if the condensate waste pipe is frozen. Water is backing up to under the boiler and overflowing there instead of backing up inside the boiler and tripping it out .
    So if the boiler is running and giving hot water and heat then, no, you don't need to reset.
    I might be wrong though.


    GSR.
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • mikey72
    mikey72 Posts: 14,680 Forumite
    Sounds like the condensate pipe is frozen, (blocked) and the water has backed up inside. Either the water is leaking out as fast as the boiler is condensing, in which case put a tray under the leak until you can defrost it, or the boiler is now filling as well, and the water is just leaking from a joint, and in which case I'm afraid it will trip eventually, unless you defrost the pipe.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.7K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.