I have read page 23 of the manual I believe is for your model. It states that the flow temp is dependant on the outdoor temperature... you can adjust this curve for -5c, 0c & +5c. Setting the temperature higher internally will not increase the flow temperature to increase the flow temp you will need to adjust the curve so that the flow temp is higher. What is it set at currently?
If you are wanting a higher temperature inside you will need to change the curve so that it responds with a higher flow temp to a not as cold outdoor temp. This will increase the running costs. You will also need to check that backup heater is not programmed to come on as well.
http://kesko-onninen-pim-resources-production.s3-website-eu-west-1.amazonaws.com/pimdocuments/DOC064186479136_IR.pdf
7.1 Tuning the heating system
To obtain a heating system balance and obtain an even and comfortable indoor temperature, the heating system may need adjustment
according to the example below.
The indoor temperature is adjusted by changing the heat curve. The heat curve calculates the supply temperature depending on the
outdoor temperature. The lower the outdoor temperature, the higher the supply temperature.
The heat curve may need to be adapted to obtain a pleasant indoor temperature in any weather conditions. A correctly set heat curve
reduces maintenance and gives an energy efficient operation.
See chapter CURVE for more information.
N
Adjust the heating system during the cold season to obtain the best possible performance.
N
Tuning must be carried out over a few days as the inertia in the heating system causes the indoor temperature to change slowly.
Tuning example
1. Choose one of the rooms, where the highest temperature is desired (20-21°C), as a reference room for the indoor temperature.
2. Place a thermometer in the room.
3. Open all radiator valves fully.
4. Leave the ROOM value set at 20°C.
See chapter ROOM for more information.
5. Note the temperature in the reference room regularly over a 24 hour period.
6. Adjust the ROOM value so that the reference room reaches your required indoor temperature of 20-21°C. Remember that other
rooms will have different temperatures during tuning, but these are adjusted later.
7. If the ROOM value must be adjusted more than 3°C upwards or downwards the CURVE value must be adjusted instead.
See chapter CURVE for more information.
8. If the indoor temperature varies several degrees despite tuning, a specific part of the heat curve may need adjusting. Check at what
outdoor temperature the variation is greatest and adjust the curve at the corresponding value (CURVE 5, CURVE 0, CURVE -5).
See chapter Adjusting the heat curve at -5°C, 0°C and 5°C for more information.
9. When the reference room has an even temperature of 20 - 21°C over a 24 hour period, you can adjust the radiator valves in the
other rooms so that their indoor temperatures are the same temperature or lower than the reference room.
7.2 CURVE
The most energy efficient and cost effective setting is achieved by changing the CURVE value to adjust the temperature in the house to
an even and constant temperature.
The control computer shows the value for CURVE by means of a graph in the display. The heat curve can be changed by adjusting the
CURVE value. The value for the CURVE indicates which value on the supply temperature is required in relation to the outdoor temperature
7.3 ROOM
If you wish to temporarily increase or reduce the indoor temperature, change the ROOM value. The difference between changing the
ROOM value and the CURVE value is as follows:
When changing the ROOM value, the angle of the curve on the system's heat curve does not change, instead the entire heat curve is
moved by 3°C for every degree change of the ROOM value.
The reason that the curve is adjusted 3°C is that an approximate 3°C increase in supply temperature is usually needed to increase the
indoor temperature 1°C.
7.4 Adjusting the CURVE at -5°C, 0°C and +5°C
Sometimes, at outdoor temperatures between -5°C and +5°C, part of the heat curve may need adjusting if the indoor temperature is not
constant. For this reason, the control system includes a function which only adjusts the heat curve at three outdoor temperatures: -5°C,
0°C and +5°C.
This function will allow one to increase or reduce the setpoint value for the supply line temperature, without affecting the rest of the
heat curve, at three specific outdoor temperatures. If, for example, the outdoor temperature is -5°C, the supply temperature will change
gradually between 0°C and -10°C, maximum adjustment being reached at -5°C.
The figure below shows the adjusted CURVE -5. The adjustment can be seen in the graph in the form of a bump. Choose to adjust the
heat curve individually at three specified outdoor temperatures: -5°C, 0°C and +5°C. The supply temperature can be changed by plus/
minus 5°C.