    I haven’t tested it as I haven’t really needed to. It’s on the least amount of time possible (twice a day) to heat the water. We have the old controls as per the picture in my initial post, the controls A&B as well as C&D are touching so that they’re on the lowest setting for time to heat the water. It’s just over an hour each time (I can’t lower them anymore unfortunately) we have plenty of hot water on the current settings and haven’t run out as of yet (there’s only 2 of us)

    Ah yes, I had an old control system when I moved in too. But I broke it so I had it replaced with a modern control system. Much easier to use and complete flexibility. Might be worth getting a quote from a gas engineer. It would also save money in the long term, as you could have the heating and hot water on at different times of the day even in winter. At the moment I guess your system is always heating the hot water if the heating is on, so that's got to waste energy.
    Changing the world, one sarcastic comment at a time.
  • weston800
    weston800 Posts: 54 Forumite
    First Anniversary Combo Breaker First Post
    stator wrote: »
    Ah yes, I had an old control system when I moved in too. But I broke it so I had it replaced with a modern control system. Much easier to use and complete flexibility. Might be worth getting a quote from a gas engineer. It would also save money in the long term, as you could have the heating and hot water on at different times of the day even in winter. At the moment I guess your system is always heating the hot water if the heating is on, so that's got to waste energy.

    Yes, if the heating is on then it's constantly heating the water too. Obviously the heating is off this time of the year but we're in the UK so could need it on again any minute! :rotfl:
  • Alex1983
    Alex1983 Posts: 958 Forumite
    Depending what your long term plans are will lead to what to do to stop it. When the time comes to change the boiler would you have a combi boiler or keep the hot water tank design? If your going to keep the hot water tank design you may as well look at converting the system to a fully pumped y or s plan system. This will give you complete independent control over hot water and heating, you will have to have it converted to this design when you have the new boiler so would not be dead money.

    If you think you would have a combi then don't spend much money on it as it will all get ripped out when you have a new boiler, the quickest and cheapest way to cure it will be to put a gate valve on the heating flow so you can isolate the heating in the summer, if this is not possible look at getting trv radiator valves that you can turn off in the summer or if the current radiator valves work ok just shut them off, that option will cost nothing but if there old they may be seized or leak. Make a note of how many turns it takes to turn off and when the time comes to turn them back on open them the same amount of turns.
  • Jonesya
    Jonesya Posts: 1,823 Forumite
    Name Dropper First Post First Anniversary Combo Breaker
    edited 22 April 2018 at 3:59PM
    I had something similar on another gravity system - it was due to a sprung non-return valve having failed (the inner part had disintegrated).

    The valve was in the hot water loop going to the radiators, normally the spring held the valve shut and stopped the natural, gravity driven flow of hot water going to the radiators (which is why only the upstairs ones got hot). When you switch on the heating, the pump starts up and the pump pressure opens the valve, heating up the radiators.

    If you can see where the pipework emerges from the boiler, or around the central heating pump area where the pipework goes off to the radiators, might be one fitted.

    Example valve:
    https://www.plumbnation.co.uk/site/full-flow-single-check-valves/
This discussion has been closed.
Meet your Ambassadors

Categories

  • All Categories
  • 343.1K Banking & Borrowing
  • 250.1K Reduce Debt & Boost Income
  • 449.7K Spending & Discounts
  • 235.2K Work, Benefits & Business
  • 607.9K Mortgages, Homes & Bills
  • 173K Life & Family
  • 247.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 15.9K Discuss & Feedback
  • 15.1K Coronavirus Support Boards