Hot Water Warm not Hot - Unvented / pressurised cylinder

RajaStyle
RajaStyle Posts: 356 Forumite
Part of the Furniture 100 Posts
Hi All

For the last 3 days the hot water is just warm not piping hot like it used to be, we shower with the temperature control completely to the max and still just warmish water comes out.

Any ideas what could be wrong ? System was put in 3 years ago with a pressurised cylinder (Elson Zircon (Baxi) the kind with a separate expansion), something I can do to resolve ?

Many Thanks in Advance

Comments

  • Consumerist
    Consumerist Posts: 6,311 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    Is it only the shower which is running cool or is all hot water the same?
    >:)Warning: In the kingdom of the blind, the one-eyed man is king.
  • RajaStyle
    RajaStyle Posts: 356 Forumite
    Part of the Furniture 100 Posts
    All the taps are the same
  • ChumpusRex
    ChumpusRex Posts: 352 Forumite
    How is the water heated?
  • RajaStyle
    RajaStyle Posts: 356 Forumite
    Part of the Furniture 100 Posts
    By the gas boiler
  • matelodave
    matelodave Posts: 8,771 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    So is the boiler actually getting hot, have you checked the boiler pressure gauge to ensure that the circulating water is adequate. Make sure the thermostat is working and check that the motorised diverter valve is opening & closing correctly.


    It appears that hot water isn't circulating in the tank heating coil so you have to find out what is going wrong. It's unlikely to be the tank itself so the problem will be with the boiler or the controls.
    Never under estimate the power of stupid people in large numbers
  • Consumerist
    Consumerist Posts: 6,311 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    Run the C/H to see if the radiators are heating properly. If they are then check the hot-water thermostat and the diverter valve operation.
    >:)Warning: In the kingdom of the blind, the one-eyed man is king.
This discussion has been closed.
Meet your Ambassadors

Categories

  • All Categories
  • 347.2K Banking & Borrowing
  • 251.6K Reduce Debt & Boost Income
  • 451.8K Spending & Discounts
  • 239.5K Work, Benefits & Business
  • 615.4K Mortgages, Homes & Bills
  • 175.1K Life & Family
  • 252.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.