Worcester Condenser Boiler
Closed Thread
Views: 17,444
Thread Tools Search this Thread Display Modes
# 1
Harloshred
Old 01-01-2009, 1:49 PM
MoneySaving Convert
 
Join Date: Jun 2006
Posts: 51
Default Worcester Condenser Boiler

Happy New Year to Everyone!

Does anyone know what Fault EA means on the boiler's display?

We've no heating or hot water.

Thanks
Harloshred is offline
Report Post
# 2
worried jim
Old 01-01-2009, 1:51 PM
Fantastically Fervent MoneySaving Super Fan
 
Join Date: Nov 2008
Posts: 5,980
Default

got this from-

http://www.diynot.com/forums/viewtopic.php?t=54114

the code is flame not detected
worried jim is offline
Report Post
The Following User Says Thank You to worried jim For This Useful Post: Show me >>
# 3
Harloshred
Old 01-01-2009, 3:29 PM
MoneySaving Convert
 
Join Date: Jun 2006
Posts: 51
Default

Thanks Jim,

Looks like it could be one of several things.
Harloshred is offline
Report Post
# 4
Harloshred
Old 01-01-2009, 6:30 PM
MoneySaving Convert
 
Join Date: Jun 2006
Posts: 51
Default

Hi,

Just to let people know that the problem was caused by a frozen flue pipe.

Might be an idea for others to check theirs.

Ours was a 22mm pipe so quite easy to freeze I suspect in the cold weather.
Harloshred is offline
Report Post
# 5
Canucklehead
Old 01-01-2009, 7:35 PM
Fantastically Fervent MoneySaving Super Fan
 
Join Date: Aug 2005
Location: South of Hadrian's Wall but London every so often.
Posts: 6,267
Default

Quote:
Originally Posted by Harloshred View Post
Hi,

Just to let people know that the problem was caused by a frozen flue pipe.

Might be an idea for others to check theirs.

Ours was a 22mm pipe so quite easy to freeze I suspect in the cold weather.
Good evening: Do you mean the condensate waste pipe had frozen? WB gives the following advice for prevention ...of course I'm assuming every RGI will follow manufacturer's specifications:rolleyes: (typical part of installation where corner cutting to keep quotation price down comes into play ).

HTH

Canucklehead
Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
Canucklehead is offline
Report Post
The Following 2 Users Say Thank You to Canucklehead For This Useful Post: Show me >>
# 6
Harloshred
Old 02-01-2009, 8:48 PM
MoneySaving Convert
 
Join Date: Jun 2006
Posts: 51
Default

Hi Canucklehead,

I do mean the condensate pipe.

We've had the pipe widened to hopefully prevent it happening again.

Thanks
Harloshred is offline
Report Post
# 7
gasbag1602
Old 03-01-2009, 11:43 AM
MoneySaving Convert
 
Join Date: Aug 2007
Posts: 192
Default

Over the holiday period i had at least 8 jobs where the problem was frozen condensate pipework they where 22mm pipe and 32mm pipe so upsizing as we all thought has not worked on these properties, i also had a one that had been lagged too! Just pooor a kettle of boiling water over the pipe where you suspect the freeze to be and you should move it!! if not another kettle should do!
gasbag1602 is offline
Report Post
The Following 2 Users Say Thank You to gasbag1602 For This Useful Post: Show me >>
# 8
yrwyddfa
Old 04-01-2009, 1:46 PM
MoneySaving Newbie
 
Join Date: Jan 2009
Posts: 9
Default EA Error Code and frozen condensate ipe

Here in N Wales wer have temps of -5 C and below and the number of boilers failing is enormous. The EA code is 'Flame not Detected' and means that the boiler will not fire. The reason is that the condensate trap cannot empty and this is caused by the pipe to the outside world being frozen.

The solution is to pour a couple of kettle fulls of hot water over the white (usually) plastic pipe untill the water thaws. Also check that there are no other bends in the system eg where it disappears into the drain.

However, a word of warning, beware of the H & S police who state you should not climb a ladder, have hot liquids in a kettle and both of these together.

On a serious note, BG have been inundated with calls and just cannot cope; so if you can cure it yourself that would be good.

All the best and a HNY
yrwyddfa is offline
Report Post
The Following User Says Thank You to yrwyddfa For This Useful Post: Show me >>
# 9
worried jim
Old 06-01-2009, 10:40 PM
Fantastically Fervent MoneySaving Super Fan
 
Join Date: Nov 2008
Posts: 5,980
Default

Glad to hear you got it working okay without major hassle/expense .
worried jim is offline
Report Post
# 10
Sally K
Old 06-01-2009, 10:54 PM
MoneySaving Newbie
 
Join Date: Jan 2009
Posts: 1
Smile Frozen consulate pipe - Worcester Bosch boiler - sorted!

BIG thank-you to canucklehead & yrwyddfa,

You've saved ( or should that be warmed?) my bacon!
Thanks to your advice I've managed to defrost my iced up pipe - it was actually under the floor in the eaves of our chalet style house!

I used a hairdryer to warm up the space - suddenly a great gurgle from the pipes - and after switching the boiler on again and re-setting it worked! I can at last take off the Puffa jacket I've been wearing all evening!

We'd been lucky enough to get a Heating Engineer out - but he said he didn't know what the code meant; was very helpful though!

It's interesting to note that Worcester Bosch have a message on their phone line about this error now!

Thanks again
Sally K is offline
Report Post
The Following User Says Thank You to Sally K For This Useful Post: Show me >>
# 11
glitter123
Old 06-01-2009, 10:59 PM
MoneySaving Stalwart
 
Join Date: Mar 2007
Posts: 478
Default

I think I might have this problem - my boiler has been making very loud gurgling noises today. Could this be a symptom of frozen condensate? Sounds like the manufacturer needs to do something about it.
glitter123 is offline
Report Post
# 12
calleyw
Old 07-01-2009, 3:06 AM
Fantastically Fervent MoneySaving Super Fan
 
Join Date: Mar 2005
Location: Winter Wonderland
Posts: 6,251
Default

Suffered this on new years eve at about 10.45pm. Was lucky I have neighbour who is corgi registered. Came and had a quick look and said thought it was frozen pipe. Came back on new years day and sorted it for us. The trap was of course full so the boiler went out.

The pipe runs out in to an outer unheated single skin porch then out side in to the down pipe. We have the boiler fitted for three years with no problems. We have had frosts nearly every night for the past 3 or 4 weeks with the day time temps not getting higher enough.

He lagged it on the inside of the porch. Nice to know (not in a nasty way as not nice have no heating or hot water) that we are not the only people to have suffered.

If we had the boiler in the bedroom suppose this would not have happened as not long enough run on the pipe to get frozen up.

Yours

Calley

Last edited by calleyw; 07-01-2009 at 3:09 AM.
calleyw is offline
Report Post
# 13
Canucklehead
Old 07-01-2009, 9:39 AM
Fantastically Fervent MoneySaving Super Fan
 
Join Date: Aug 2005
Location: South of Hadrian's Wall but London every so often.
Posts: 6,267
Default

Quote:
Originally Posted by Sally K View Post
BIG thank-you to canucklehead & yrwyddfa,

You've saved ( or should that be warmed?) my bacon!
Thanks to your advice I've managed to defrost my iced up pipe - it was actually under the floor in the eaves of our chalet style house!

I used a hairdryer to warm up the space - suddenly a great gurgle from the pipes - and after switching the boiler on again and re-setting it worked! I can at last take off the Puffa jacket I've been wearing all evening!

We'd been lucky enough to get a Heating Engineer out - but he said he didn't know what the code meant; was very helpful though!

It's interesting to note that Worcester Bosch have a message on their phone line about this error now!

Thanks again
You're welcome Worcester Bosch now have a section on their website about frozen condensate pipes

My OH hasn't had any calls from customers for his Vaillants or Viessmanns...fingers crossed

HTH

Canucklehead
Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
Canucklehead is offline
Report Post
# 14
glitter123
Old 07-01-2009, 10:02 AM
MoneySaving Stalwart
 
Join Date: Mar 2007
Posts: 478
Default

That was my problem too. Plumber is adapting the pipework as I type.
glitter123 is offline
Report Post
# 15
Norroy
Old 06-01-2010, 3:33 PM
MoneySaving Convert
 
Join Date: Dec 2005
Posts: 93
Default

The above posts almost exactly describe the problems I am having with my Worcester Greenstar. I know Worcester are blaming shoddy workmanship, but it sounds to me like a design fault on their part, especially if Vaillant condensing boilers aren't doing the same thing.

My boiler is one storey up with another flat below. Hopefully my heating engineer will be able to reach out and get to it.
Norroy is offline
Report Post
# 16
mikey72
Old 06-01-2010, 4:32 PM
Deliciously Dedicated Diehard MoneySaving Devotee
 
Join Date: Jul 2008
Posts: 14,412
Default

They all do it.
The Worcester actually have a syphon type arrangement to empty in 100ml or so at a time, most of the others just drip continuously.
So in theory the Worcester ones should freeze less. Be interesting to know if it actually makes the problem worse.
Having said that the Ariston I fitted years ago has never had a problem either.
(with anything)
I have seen some really bad pipe runs by RGI's that cause problems on condensate pipes though. I've got one to change when it warms up a bit.

Last edited by mikey72; 06-01-2010 at 4:34 PM.
mikey72 is offline
Report Post
# 17
nathanmdrew
Old 07-01-2010, 7:37 PM
MoneySaving Newbie
 
Join Date: Jan 2010
Posts: 1
Default Frozen Condensate Pipe

Hey,
my combi boiler stopped working earlier today, the error message said the flame was not firing, when I reset the boiler it tried firing up for a few seconds then stopped again.
I called a boiler repair man, the cheapest quote was £75+vat to come out!!!
I then figured it must be all due to this extreme cold weather, as I've had it for 3 years and no problems. I then looked at the manual which said the error message either meant the flame detection electrode was broken (sounds expensive), or the condensate pipe was blocked or frozen. I then found this thread your reading now, and did what everyone was suggesting, not expecting it to work really...... I simply boiled a kettle, poured it over the condensate pipe, pressed the reset button, said a prayer, and amazingly it worked straight away - I could hear the water gushing and flowing like it was breaking free fom the pipe coming out the underneath of the boiler!
(Note, I poured the water on outdoors part of the pipe only!)
If your searching for an answer to the same problem, reading this message could save you £90
nathanmdrew is offline
Report Post
# 18
mikey72
Old 07-01-2010, 8:54 PM
Deliciously Dedicated Diehard MoneySaving Devotee
 
Join Date: Jul 2008
Posts: 14,412
Default

Just been out and done another one, frozen solid over today, just quit tonight.
mikey72 is offline
Report Post
# 19
RealJC
Old 07-01-2010, 11:33 PM
MoneySaving Newbie
 
Join Date: Jan 2010
Posts: 2
Default

I thought I'd share with you my experience with my Worcester boiler and its condensate pipe.

Had the boiler nearly four years, no problem. Then comes the current big freeze and tonight I get home to no power in the house. Odd thinks I, so switches everything back on at the consumer unit, goes back into the house to find a flooded kitchen and a considerable amount of water dripping from underneath the boiler.

Thought this was due to something in the boiler breaking, but in fact was due to how the condensate pipe is fitted, and the current cold snap. Whilst the condensate pipe itself is not frozen, the fall pipe to which the condensate pipe attaches is frozen at the bottom. This blockage caused any melt water, condensate and anything else in the pipe to back up the fall pipe, the condensate pipe and into the boiler. It proceeded to fill up the fan, heat exchanger, gas valve, the whole thing. It was this that tripped the electrics in the house. Right now I have a partly flooded kitchen and a bolier in bits overnight - will be a cold one for sure!

Folks, anyone who's condensate joins to another pipe please do check that it is not getting frozen up, otherwise you could an up with water backing into your boiler...

I have a feeling that this is a risk with any fall pipes that don't carry much waste (as with the offending one of mine), with the small amounts of condensate, plus a little melt water, building up frozen layers over time until it is blocked.

All the best,

RealJC
RealJC is offline
Report Post
# 20
M271
Old 08-01-2010, 9:46 AM
MoneySaving Convert
 
Join Date: May 2006
Location: Southampton
Posts: 150
Default

Quote:
Originally Posted by RealJC View Post
I thought I'd share with you my experience with my Worcester boiler and its condensate pipe.

Had the boiler nearly four years, no problem. Then comes the current big freeze and tonight I get home to no power in the house. Odd thinks I, so switches everything back on at the consumer unit, goes back into the house to find a flooded kitchen and a considerable amount of water dripping from underneath the boiler.

Thought this was due to something in the boiler breaking, but in fact was due to how the condensate pipe is fitted, and the current cold snap. Whilst the condensate pipe itself is not frozen, the fall pipe to which the condensate pipe attaches is frozen at the bottom. This blockage caused any melt water, condensate and anything else in the pipe to back up the fall pipe, the condensate pipe and into the boiler. It proceeded to fill up the fan, heat exchanger, gas valve, the whole thing. It was this that tripped the electrics in the house. Right now I have a partly flooded kitchen and a bolier in bits overnight - will be a cold one for sure!

Folks, anyone who's condensate joins to another pipe please do check that it is not getting frozen up, otherwise you could an up with water backing into your boiler...

I have a feeling that this is a risk with any fall pipes that don't carry much waste (as with the offending one of mine), with the small amounts of condensate, plus a little melt water, building up frozen layers over time until it is blocked.

All the best,

RealJC
I had the same problem on my Worcestershire Bosch 18Ri overnight (-12c), the condensate pipe from the boiler was not frozen but further down the outlet pipe from the sink to the outside was.

Fortunately I can detach my condensate tube where it exits the bottom of the boiler and the boiler is now working by dumping the condensate into a washing up bowl, when conditions improve I'll connect the tube back up.
M271 is offline
Report Post
Closed Thread

Bookmarks
 
 




Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

 Forum Jump  

Contact Us - MoneySavingExpert.com - Archive - Privacy Statement - Top

Powered by vBulletin® Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.

All times are GMT. The time now is 3:26 AM.

 Forum Jump  

Free MoneySaving Email

Top deals: Week of 29 October 2014

Get all this & more in MoneySavingExpert's weekly email full of guides, vouchers and Deals

GET THIS FREE WEEKLY EMAIL Full of deals, guides & it's spam free

Latest News & Blogs

Martin's Twitter Feed

profile

Cheap Travel Money

Find the best online rate for holiday cash with MSE's TravelMoneyMax.

Find the best online rate for your holiday cash with MoneySavingExpert's TravelMoneyMax.

TuneChecker Top Albums

  • VARIOUS ARTISTSBBC RADIO 1'S LIVE LOUNGE 2014
  • TAYLOR SWIFT1989 (DELUXE)
  • ED SHEERANX (DELUXE EDITION)

MSE's Twitter Feed

profile
Always remember anyone can post on the MSE forums, so it can be very different from our opinion.
We use Skimlinks and other affiliated links in some of our boards, for some of our users.