    got this from-

    http://www.diynot.com/forums/viewtopic.php?t=54114

    the code is flame not detected
  • Harloshred
    • #3
    • 1st Jan 09, 3:29 PM
    • #3
    • 1st Jan 09, 3:29 PM
    Thanks Jim,

    Looks like it could be one of several things.
  • Harloshred
    • #4
    • 1st Jan 09, 6:30 PM
    • #4
    • 1st Jan 09, 6:30 PM
    Hi,

    Just to let people know that the problem was caused by a frozen flue pipe.

    Might be an idea for others to check theirs.

    Ours was a 22mm pipe so quite easy to freeze I suspect in the cold weather.
  • Canucklehead
    • #5
    • 1st Jan 09, 7:35 PM
    • #5
    • 1st Jan 09, 7:35 PM
    Hi,

    Just to let people know that the problem was caused by a frozen flue pipe.

    Might be an idea for others to check theirs.

    Ours was a 22mm pipe so quite easy to freeze I suspect in the cold weather.
    Originally posted by Harloshred
    Good evening: Do you mean the condensate waste pipe had frozen? WB gives the following advice for prevention ...of course I'm assuming every RGI will follow manufacturer's specifications:rolleyes: (typical part of installation where corner cutting to keep quotation price down comes into play ).

    HTH

    Canucklehead
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • Harloshred
    • #6
    • 2nd Jan 09, 8:48 PM
    • #6
    • 2nd Jan 09, 8:48 PM
    Hi Canucklehead,

    I do mean the condensate pipe.

    We've had the pipe widened to hopefully prevent it happening again.

    Thanks
  • gasbag1602
    • #7
    • 3rd Jan 09, 11:43 AM
    • #7
    • 3rd Jan 09, 11:43 AM
    Over the holiday period i had at least 8 jobs where the problem was frozen condensate pipework they where 22mm pipe and 32mm pipe so upsizing as we all thought has not worked on these properties, i also had a one that had been lagged too! Just pooor a kettle of boiling water over the pipe where you suspect the freeze to be and you should move it!! if not another kettle should do!
  • yrwyddfa
    • #8
    • 4th Jan 09, 1:46 PM
    EA Error Code and frozen condensate ipe
    • #8
    • 4th Jan 09, 1:46 PM
    Here in N Wales wer have temps of -5 C and below and the number of boilers failing is enormous. The EA code is 'Flame not Detected' and means that the boiler will not fire. The reason is that the condensate trap cannot empty and this is caused by the pipe to the outside world being frozen.

    The solution is to pour a couple of kettle fulls of hot water over the white (usually) plastic pipe untill the water thaws. Also check that there are no other bends in the system eg where it disappears into the drain.

    However, a word of warning, beware of the H & S police who state you should not climb a ladder, have hot liquids in a kettle and both of these together.

    On a serious note, BG have been inundated with calls and just cannot cope; so if you can cure it yourself that would be good.

    All the best and a HNY
  • worried jim
    • #9
    • 6th Jan 09, 10:40 PM
    • #9
    • 6th Jan 09, 10:40 PM
    Glad to hear you got it working okay without major hassle/expense .
  • Sally K
    Frozen consulate pipe - Worcester Bosch boiler - sorted!
    BIG thank-you to canucklehead & yrwyddfa,

    You've saved ( or should that be warmed?) my bacon!
    Thanks to your advice I've managed to defrost my iced up pipe - it was actually under the floor in the eaves of our chalet style house!

    I used a hairdryer to warm up the space - suddenly a great gurgle from the pipes - and after switching the boiler on again and re-setting it worked! I can at last take off the Puffa jacket I've been wearing all evening!

    We'd been lucky enough to get a Heating Engineer out - but he said he didn't know what the code meant; was very helpful though!

    It's interesting to note that Worcester Bosch have a message on their phone line about this error now!

    Thanks again
  • glitter123
    I think I might have this problem - my boiler has been making very loud gurgling noises today. Could this be a symptom of frozen condensate? Sounds like the manufacturer needs to do something about it.
    • calleyw
    • By calleyw 7th Jan 09, 3:06 AM
    • 7,358 Posts
    • 11,942 Thanks
    calleyw
    Suffered this on new years eve at about 10.45pm. Was lucky I have neighbour who is corgi registered. Came and had a quick look and said thought it was frozen pipe. Came back on new years day and sorted it for us. The trap was of course full so the boiler went out.

    The pipe runs out in to an outer unheated single skin porch then out side in to the down pipe. We have the boiler fitted for three years with no problems. We have had frosts nearly every night for the past 3 or 4 weeks with the day time temps not getting higher enough.

    He lagged it on the inside of the porch. Nice to know (not in a nasty way as not nice have no heating or hot water) that we are not the only people to have suffered.

    If we had the boiler in the bedroom suppose this would not have happened as not long enough run on the pipe to get frozen up.

    Yours

    Calley
    Last edited by calleyw; 07-01-2009 at 3:09 AM.
  • Canucklehead
    BIG thank-you to canucklehead & yrwyddfa,

    You've saved ( or should that be warmed?) my bacon!
    Thanks to your advice I've managed to defrost my iced up pipe - it was actually under the floor in the eaves of our chalet style house!

    I used a hairdryer to warm up the space - suddenly a great gurgle from the pipes - and after switching the boiler on again and re-setting it worked! I can at last take off the Puffa jacket I've been wearing all evening!

    We'd been lucky enough to get a Heating Engineer out - but he said he didn't know what the code meant; was very helpful though!

    It's interesting to note that Worcester Bosch have a message on their phone line about this error now!

    Thanks again
    Originally posted by Sally K
    You're welcome Worcester Bosch now have a section on their website about frozen condensate pipes

    My OH hasn't had any calls from customers for his Vaillants or Viessmanns...fingers crossed

    HTH

    Canucklehead
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • glitter123
    That was my problem too. Plumber is adapting the pipework as I type.
  • Norroy
    The above posts almost exactly describe the problems I am having with my Worcester Greenstar. I know Worcester are blaming shoddy workmanship, but it sounds to me like a design fault on their part, especially if Vaillant condensing boilers aren't doing the same thing.

    My boiler is one storey up with another flat below. Hopefully my heating engineer will be able to reach out and get to it.
  • mikey72
    They all do it.
    The Worcester actually have a syphon type arrangement to empty in 100ml or so at a time, most of the others just drip continuously.
    So in theory the Worcester ones should freeze less. Be interesting to know if it actually makes the problem worse.
    Having said that the Ariston I fitted years ago has never had a problem either.
    (with anything)
    I have seen some really bad pipe runs by RGI's that cause problems on condensate pipes though. I've got one to change when it warms up a bit.
    Last edited by mikey72; 06-01-2010 at 4:34 PM.
  • nathanmdrew
    Frozen Condensate Pipe
    Hey,
    my combi boiler stopped working earlier today, the error message said the flame was not firing, when I reset the boiler it tried firing up for a few seconds then stopped again.
    I called a boiler repair man, the cheapest quote was 75+vat to come out!!!
    I then figured it must be all due to this extreme cold weather, as I've had it for 3 years and no problems. I then looked at the manual which said the error message either meant the flame detection electrode was broken (sounds expensive), or the condensate pipe was blocked or frozen. I then found this thread your reading now, and did what everyone was suggesting, not expecting it to work really...... I simply boiled a kettle, poured it over the condensate pipe, pressed the reset button, said a prayer, and amazingly it worked straight away - I could hear the water gushing and flowing like it was breaking free fom the pipe coming out the underneath of the boiler!
    (Note, I poured the water on outdoors part of the pipe only!)
    If your searching for an answer to the same problem, reading this message could save you 90
  • mikey72
    Just been out and done another one, frozen solid over today, just quit tonight.
  • RealJC
    I thought I'd share with you my experience with my Worcester boiler and its condensate pipe.

    Had the boiler nearly four years, no problem. Then comes the current big freeze and tonight I get home to no power in the house. Odd thinks I, so switches everything back on at the consumer unit, goes back into the house to find a flooded kitchen and a considerable amount of water dripping from underneath the boiler.

    Thought this was due to something in the boiler breaking, but in fact was due to how the condensate pipe is fitted, and the current cold snap. Whilst the condensate pipe itself is not frozen, the fall pipe to which the condensate pipe attaches is frozen at the bottom. This blockage caused any melt water, condensate and anything else in the pipe to back up the fall pipe, the condensate pipe and into the boiler. It proceeded to fill up the fan, heat exchanger, gas valve, the whole thing. It was this that tripped the electrics in the house. Right now I have a partly flooded kitchen and a bolier in bits overnight - will be a cold one for sure!

    Folks, anyone who's condensate joins to another pipe please do check that it is not getting frozen up, otherwise you could an up with water backing into your boiler...

    I have a feeling that this is a risk with any fall pipes that don't carry much waste (as with the offending one of mine), with the small amounts of condensate, plus a little melt water, building up frozen layers over time until it is blocked.

    All the best,

    RealJC
  • M271
    I thought I'd share with you my experience with my Worcester boiler and its condensate pipe.

    Had the boiler nearly four years, no problem. Then comes the current big freeze and tonight I get home to no power in the house. Odd thinks I, so switches everything back on at the consumer unit, goes back into the house to find a flooded kitchen and a considerable amount of water dripping from underneath the boiler.

    Thought this was due to something in the boiler breaking, but in fact was due to how the condensate pipe is fitted, and the current cold snap. Whilst the condensate pipe itself is not frozen, the fall pipe to which the condensate pipe attaches is frozen at the bottom. This blockage caused any melt water, condensate and anything else in the pipe to back up the fall pipe, the condensate pipe and into the boiler. It proceeded to fill up the fan, heat exchanger, gas valve, the whole thing. It was this that tripped the electrics in the house. Right now I have a partly flooded kitchen and a bolier in bits overnight - will be a cold one for sure!

    Folks, anyone who's condensate joins to another pipe please do check that it is not getting frozen up, otherwise you could an up with water backing into your boiler...

    I have a feeling that this is a risk with any fall pipes that don't carry much waste (as with the offending one of mine), with the small amounts of condensate, plus a little melt water, building up frozen layers over time until it is blocked.

    All the best,

    RealJC
    Originally posted by RealJC
    I had the same problem on my Worcestershire Bosch 18Ri overnight (-12c), the condensate pipe from the boiler was not frozen but further down the outlet pipe from the sink to the outside was.

    Fortunately I can detach my condensate tube where it exits the bottom of the boiler and the boiler is now working by dumping the condensate into a washing up bowl, when conditions improve I'll connect the tube back up.
Welcome to our new Forum!

Our aim's to save you money quickly and easily. We hope you like it!

Forum Team Contact us

Live Stats

2,283Posts Today

7,724Users online

Martin's Twitter
  • Thanks to @CBBC_Hacker for sending us our own Hacker, baby MSE is smitten. Altight cocker. http://t.co/mdVVz56YHD

  • RT @MoneySavingExp: Hi folks - the site will be down from 10pm tonight until 8am tomorrow while we re-charge the batteries with some behind?

  • Uk dominating world long jump.Who'd have thought it. Kathy Cook's British 200m record about to go I think. #Beijing2015

  • Follow Martin