Central heating problem

2

Comments

  • BoxerfanUK
    BoxerfanUK Posts: 688 Forumite
    Photogenic First Post First Anniversary
    edited 18 October 2016 at 6:53PM
    I had a similar problem recently and we have separate zones for up and downstairs.

    When the heating came on only the upstairs radiators got hot, cold downstairs. Manually moved the slider across on the zone valve and downstairs radiators came on but obviously the downstairs radiators then came on when the boiler fired up for the hot water as the zone valve was now manually open all the time.

    I suspected it could be a faulty Synchron motor in the zone valve so bought a new one from Screwfix for £16.00, problem solved. A lot cheaper than calling a plumber out and draining the system down to replace a complete zone valve when just the motor was at fault. This is quite a common problem.

    http://www.screwfix.com/p/drayton-synchronous-motor/28670
  • Annie1960
    Annie1960 Posts: 3,002 Forumite
    First Anniversary Name Dropper First Post Combo Breaker
    Le_Kirk wrote: »
    They are zone valves, so you probably have separate upstairs and downstairs heating circuits. If they are exactly like that then the bit that has an arrow pointing to it saying "auxiliary end switch" is also a manual override, you open the valve by moving the slider to the right and tucking it behind the little catch above it. What is supposed to happen is that next time power is applied the valve closes. Is your boiler a combi or do you have a hot water storage cylinder?

    Boiler is Worcester Bosch, not a combi, i think it's called a 'heat only' boiler.
  • Rubidium
    Rubidium Posts: 663 Forumite
    First Post
    Annie1960 wrote: »
    Boiler is Worcester Bosch, not a combi, i think it's called a 'heat only' boiler.

    The first plumber may have diagnosed the problem correctly and the timer/programmer could need replacing - this can easily be proved with a multi-meter.

    You would know if you had two zones for your heating as you would likely have two thermostats, one for each zone.

    It is more likely that one valve is for hot water and the other for heating.

    Your problem is that most plumbers don't do electrics and most sparks don't touch wet stuff.
  • Risteard
    Risteard Posts: 1,885 Forumite
    First Anniversary Name Dropper First Post
    Annie1960 wrote: »
    Have looked in airing cupboard. I recognise the pump. There are also two other things with Honeywell on them. Not sure if either one of these is the 3-point diverter valve you mention.

    How will I recognise it? I can't see H, M or W.
    Presumably it is an S-plan you have rather than Y-plan. I'm not sure why others jumped to the conclusion that it was Y-plan.
    RECI & Safe Electric Registered Electrical Contractor
    NICEIC Approved Contractor
    ECA Registered Member
  • Risteard
    Risteard Posts: 1,885 Forumite
    First Anniversary Name Dropper First Post
    Rubidium wrote: »
    Your problem is that most plumbers don't do electrics
    And the ones that do shouldn't. I've never seen good electrical work by a plumber yet. Absolute jokers.
    RECI & Safe Electric Registered Electrical Contractor
    NICEIC Approved Contractor
    ECA Registered Member
  • Risteard wrote: »
    Presumably it is an S-plan you have rather than Y-plan. I'm not sure why others jumped to the conclusion that it was Y-plan.

    I'm guessing it's because y plans are far more common maybe
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • bsod
    bsod Posts: 1,225 Forumite
    edited 18 October 2016 at 11:31PM
    what model is the timer

    is the room thermostat set to call for heat

    press the hot water timer on button, and trace which pipes get hot by feel (carefully), then check the position of the lever on the valves.
    Don't you dare criticise what you cannot understand
  • Risteard
    Risteard Posts: 1,885 Forumite
    First Anniversary Name Dropper First Post
    I'm guessing it's because y plans are far more common maybe
    I would say S-plans are far and away more common here to be honest.
    RECI & Safe Electric Registered Electrical Contractor
    NICEIC Approved Contractor
    ECA Registered Member
  • Annie1960
    Annie1960 Posts: 3,002 Forumite
    First Anniversary Name Dropper First Post Combo Breaker
    Risteard wrote: »
    Presumably it is an S-plan you have rather than Y-plan. I'm not sure why others jumped to the conclusion that it was Y-plan.

    I have no idea what this means.
  • FreeBear
    FreeBear Posts: 14,620 Forumite
    First Anniversary First Post Name Dropper Photogenic
    Annie1960 wrote: »
    I have no idea what this means.

    There are different ways of plumbing in a combined central heating and hot water tank. The most common arrangements are fully pumped S plan, Y plan, and gravity systems. For most home owners, the technical details are of little importance as long as the system works and a plumber can fix it.

    Google can provide an answer if you really want to know the finer points about each system. But your eyes may glaze over once you start looking.
    Her courage will change the world.

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
This discussion has been closed.
Meet your Ambassadors

Categories

  • All Categories
  • 343.2K Banking & Borrowing
  • 250.1K Reduce Debt & Boost Income
  • 449.7K Spending & Discounts
  • 235.3K Work, Benefits & Business
  • 608K Mortgages, Homes & Bills
  • 173.1K Life & Family
  • 247.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 15.9K Discuss & Feedback
  • 15.1K Coronavirus Support Boards