New stronger floor in loft space

Options
Evening all, would REALLY appreciate some help on the following.

First off, basic floor plan of the loft:

d8319de2.jpg

Hard lines are the walls on the first floor underneath, joists on the first floor landing run left to right so does that mean the central wall running front to back is 'load bearing'? Total loft dimensions are 5.2m left to right, 7m front to back.

Next up, photo of one of the corners, bottom right corner on the floor plan, taken from near the hatch:

d9029133.jpg

You can see the 4x2 ceiling joists and another 4x2 going left to right (ceiling binder?) that appears to be nailed to the bottom of the roof rafter and then sits up against the chimney breast on the opposed side of the loft (semi detached house) but not actually tied into anything.

So here's my problem. I want to put down new deeper floor joists so I can use it for heavier storage and possibly a hobby room of some kind in the future.

Initially I thought of putting 8x2s front to back, supporting them on internal walls where possible. Problem is that the angle of the eaves would not allow me to rest the ends on anything substantial so could I just bolt them to the rafters as long as they were supported by the walls downstairs too?

Then I got thinking that I'd need to go left to right .. a) because the load bearing walls go down the centre of the house and b) because if I don't the ceiling binder will be in the way. Same problem however with regards to getting the joists to sit on the external walls and I'm guessing I'm not allowed to bolt a plate to the chimney wall and hang things off that.

So, I'm after ideas people, what you got? :-)

Cheers!
Monty
«1

Comments

  • jc808
    jc808 Posts: 1,756 Forumite
    Options
    I beefed up my loft with 8x2 laid at right angles to 4x2 ceiling joists

    8x2s were nailed to the joists but not tied into the walls or roof.
    This was so I could add 270mm insulation

    I then floored the loft with T+G and plasterboarded the ceilings below

    Floor is as strong/ inflexible as ant other floor in my house - do it!
  • foolishboy
    foolishboy Posts: 321 Forumite
    Options
    jc808 wrote: »
    I beefed up my loft with 8x2 laid at right angles to 4x2 ceiling joists

    8x2s were nailed to the joists but not tied into the walls or roof.
    This was so I could add 270mm insulation

    I then floored the loft with T+G and plasterboarded the ceilings below

    Floor is as strong/ inflexible as ant other floor in my house - do it!

    ..I'd love to just do that but what is taking the extra load from the timber you've added? It sounds like it's just sitting on the ceiling joists and not supported by anything structural. Or did I miss something? :-)

    Cheers!
  • jc808
    jc808 Posts: 1,756 Forumite
    Options
    foolishboy wrote: »
    ..I'd love to just do that but what is taking the extra load from the timber you've added? It sounds like it's just sitting on the ceiling joists and not supported by anything structural. Or did I miss something? :-)

    Cheers!

    Youre right - the dead load of the T+G flooring, insulation and the 8x2 is all extra load on the joists only.

    However its not a room per se, just a light storage space

    And the fact all the boards, crossbatten 8x2s and T+G flooring are screwed together, the whole lot is tied together. Its not going anywhere. Its when you have large loads on 1 or 2 joists only you will get flex. As soon as you step into my loft, your weight is distributed across every joist, so no flex

    It wouldnt be fit for permanent habitation though, light storage/ occasional use is OK
  • 27col
    27col Posts: 6,554 Forumite
    Options
    There is no point in adding joists unless they are supported at their ends.They need to sit on the inner skin of the cavity wall. If you can provide more support from load bearing walls, so much the better. If the new joists are not supported at their ends then all they are doing is adding weight to the existing joists.
    I can afford anything that I want.
    Just so long as I don't want much.
  • foolishboy
    foolishboy Posts: 321 Forumite
    Options
    27col wrote: »
    There is no point in adding joists unless they are supported at their ends.They need to sit on the inner skin of the cavity wall. If you can provide more support from load bearing walls, so much the better. If the new joists are not supported at their ends then all they are doing is adding weight to the existing joists.

    Agreed ... but how do I go about supporting them on the ends when the level of the cavity wall inner skin isn't accessible due to the angle of the eaves?

    http://s1188.photobucket.com/albums/z403/monty77uk/loft/?action=view&current=8ce49f0a.jpg

    ...must be a way around this surely?

    Thanks :-)
    FB
  • foolishboy
    foolishboy Posts: 321 Forumite
    Options
    jc808 wrote: »
    Youre right - the dead load of the T+G flooring, insulation and the 8x2 is all extra load on the joists only.

    However its not a room per se, just a light storage space

    And the fact all the boards, crossbatten 8x2s and T+G flooring are screwed together, the whole lot is tied together. Its not going anywhere. Its when you have large loads on 1 or 2 joists only you will get flex. As soon as you step into my loft, your weight is distributed across every joist, so no flex

    It wouldnt be fit for permanent habitation though, light storage/ occasional use is OK

    Fair enough .. I just figured if I was about to spend a ton of £££ on large timbers and flooring I'd at least make it as strong as possible but perhaps it's not realistic.

    Cheers!
    FB
  • vaio
    vaio Posts: 12,287 Forumite
    First Post First Anniversary Combo Breaker
    Options
    foolishboy wrote: »
    Agreed ... but how do I go about supporting them on the ends when the level of the cavity wall inner skin isn't accessible due to the angle of the eaves?

    http://s1188.photobucket.com/albums/z403/monty77uk/loft/?action=view&current=8ce49f0a.jpg

    ...must be a way around this surely?

    Thanks :-)

    Cut the ends of the new joists so they fit on the existing wall plate just as the existing joists/rafters do?
  • foolishboy
    foolishboy Posts: 321 Forumite
    Options
    vaio wrote: »
    Cut the ends of the new joists so they fit on the existing wall plate just as the existing joists/rafters do?

    Is that what they're sitting on? It feels like wood, I thought the wall plate would be slate/stone. Also by the time I've cut it at an angle very little of it will likely be actually sitting on the plate. Plus I'll want to put the new joists 15-20mm raised anyway to keep them away from the existing ceiling.

    Cheers,
    FB
  • vaio
    vaio Posts: 12,287 Forumite
    First Post First Anniversary Combo Breaker
    Options
    the wall plate will be wood. Cutting the new joists to an angle will be fine, the loads at the end are essentially shear and you don't need much wood to cope with the sort of shear loads you'll be applying.

    Bending is more of problem, if you can block down onto the load bearing wall then your span looks like about 3m in which case 6 x 2 will be fine.

    If you want to rise them up 20 or 30mm to get them away from the existing ceiling then cut some bits of ply to use as spacers on the wall plates. Same idea can be used to transfer loads onto the spine wall
  • foolishboy
    foolishboy Posts: 321 Forumite
    Options
    vaio wrote: »
    the wall plate will be wood. Cutting the new joists to an angle will be fine, the loads at the end are essentially shear and you don't need much wood to cope with the sort of shear loads you'll be applying.

    Bending is more of problem, if you can block down onto the load bearing wall then your span looks like about 3m in which case 6 x 2 will be fine.

    If you want to rise them up 20 or 30mm to get them away from the existing ceiling then cut some bits of ply to use as spacers on the wall plates. Same idea can be used to transfer loads onto the spine wall

    Top man .. all getting a lot clearer. So going front to back will be fine? If so span is about 3.9m so will be using 8x2 to be safe I think.

    Only confusion now is the ceiling binder which will be totally in the way as it is now. What do I have to do to allow me to replace that? Noggin the ceiling joists? Or bolt the new joists to ceiling joists?

    Cheers,
    FB
This discussion has been closed.
Meet your Ambassadors

Categories

  • All Categories
  • 12 Election 2024: The MSE Leaders' Debate
  • 344K Banking & Borrowing
  • 250.3K Reduce Debt & Boost Income
  • 450.1K Spending & Discounts
  • 236.1K Work, Benefits & Business
  • 609.4K Mortgages, Homes & Bills
  • 173.5K Life & Family
  • 248.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 15.9K Discuss & Feedback
  • 15.1K Coronavirus Support Boards